APC UPS charging problem
After following the help provided here I was able to get the UPS working again. YEY !!! Now I get good numbers: Mains disconnected and UPS off - PowerChute "Disconnected" 0.009A 12.72v Mains connected and UPS off - PowerChute "Charging" Negative 0.7A 12v+ and rising Mains connected and UPS on - PowerChute "Charging" Negative 0.55A 12v+ and rising - no decrease in % over time as before ๐ Mains disconnected and UPS on - PowerChute "Discharging" -6.6A 11.98v (60W lamp) - battery slowly discharges as expected Connected mains back resutls are same as in (3) above.
-
APC UPS charging problem
So I charged the battery with the battery charger. Placed in the UPS Updated date Connected to Mains with no load and UPS on And waited... After 4 days the battery decreased to 46%. 7% every 12 hours (in jumps of 7% - not 1% at a time) To make sure it was not just a report error by the UPS or PowerChute SW I connectred it again to the battery charger and indeed the battery was drained down to ~50%. So I have a faulty UPS - leaking battery power to somewhere... and UPS not charging the battery when it is ON. I will probably have to buy a new UPS ๐
-
APC UPS charging problem
I drained the battery completely and used a borrowed battery charger (SON-1206D) to charge the battery. It reached 13.6v after full charge (took slightly more than 1 hour @ 6A). I then connected to UPS and again fully discharged the battery and then started to charge via UPS. Charging current is still very low ~0.2A. Edit: Looking again, carefully his timm, at the UPS specificationns I saw https://www.se.com/il/en/product/BR550GI/apc-powersaving-backups-pro-550/ So maybe the 0.2A (sometimes went up to 0.3-0.35A) could be OK assuming charging voltage is ~14.0-14.5V (5W/14.5V = 0.35A)
- APC UPS charging problem
-
APC UPS charging problem
OK, so I did some measurements and here they are (battery at >95% when started test): No load: Mains disconnected and UPS off - PowerChute "Disconnected" 0.00A 12.76v Mains connected and UPS off - PowerChute "Charging" Negative 0.02-0.04A 12.89v Mains connected and UPS on - PowerChute "Charging" 0.09-0.12A 12.77v - battery % is decreasing slowly Mains disconnected and UPS on - PowerChute "Discharging" 0.45A-0.60A 12.49v - battery % dropped almost immediately by 10% Connected mains back resutls are same as in (3) above. Repeated and same thing happened (including the % drop - 7% this time) With 60W (lamp) load: Mains disconnected and UPS off - PowerChute "Disconnected" 0.07A-0.05A 12.72v Mains connected and UPS off - PowerChute "Charging" Negative 0.02-0.04A 12.81v Mains connected and UPS on - PowerChute "Charging" 0.09-0.12A 12.68v - during the power on I get 4.8A Mains disconnected and UPS on - PowerChute "Discharging" 4.82A-5.25A 11.98v - battery slowly decreases Connected mains back resutls are same as in (3) above. Turned UPS OFF and ON again and am seeing 0.15A-0.17A. I think the only time I get charging (Negative current) is "With Load" and "Mains connected and UPS off" But that is VERY low charging current... In both (3) although PowerChute says charging I have a positive current meaning discharging. So it seems that my UPS is only charging when OFF and at a VERY slow rate. What could be the problem?
-
APC UPS charging problem
Even if it was wrongly activated, and there is no load, why would the battery drain? where to?
-
APC UPS charging problem
Amp clamp meter on battery leads? I disconnected mains and battery more than once, also did logic reset procedure (press power on a few seconds when all is disconnected) and it did not help. UPS does not seem to be stuck in battery mode because when I do self test I can here the clicking of the relays from mains to battery and back.
-
APC UPS charging problem
Hi, I have an BR550GI Back-UPS pro APC UPS for a few years. Recently I replaced the battery (not the first time) and am having strange issues with the UPS. I charged the battery for several hours to make sure it is full. The issues I am seeing (UPS is connected to PC with PowerChute SW for diagnostics): When connecting to a load (lamp/Computer - tried both) and UPS is connected to AC mains the capacity % goes down in jumps of ~7% over hours (not one percent at a time). When disconnecting the load and UPS is still connected to AC mains the UPS does not charge the battery. % keeps dropping same as previously. What can be the problem? Notes: When powering off the UPS and UPS is connected to AC mains the UPS does charge the battery (% goes up slowly until it reaches 100%) opened the unit and saw no swelling in capacitors
-
[SOLVED] GPU Passthrough issue: BAR 0: can't reserve
Thanks adding these line work !!! What do they actually do?
-
** VIDEO GUIDE - How to Easily Dump a vBIOS from any GPU directly from the Server for passthrough
If I have an Nvidia gpu (single gpu and no igpu). Do I need it to be binded in vfid-pci or not when running this script? When I complete this process fully (have dumped vbios) do I need to bind the gpu or can I leave it unbinded so I can use it for unraid until my VM is started and after vm is shut down?
-
Windows 11 System Requirements Announced - does it pose any issues?
I just ran a Windows 11 compatibility check on my working Windows 10 VM (OVMF BIOS) using Microsoft PC Health Check tool and recieved the following incombatibility error. "The PC must support Secure Boot" Does this mean I cannot / will not be able to upgrade to Windows 11?
-
Odd Ngnix error filling up my syslog
I uninstalled the unraid.net plugin and problem "fixed"
-
[Support] Linuxserver.io - Qbittorrent
Can Flood (https://flood.js.org/) be run in this docker?
-
Odd Ngnix error filling up my syslog
The "problem" is that I have no other PC or smartphone currently open with an unRAID webUI tab open.
-
Odd Ngnix error filling up my syslog
I am having the same issue - message in syslog everey 1-2 seconds from 10:31:28 to 12:30:28 and suddenly stopped. What is a "stale" web GUI tab? why is it defined as stale. I am also getting the following errors also related to nginx every minute in between the "nginx worker process" messages: May 21 12:30:20 Tower nginx: 2021/05/21 12:30:20 [error] 29362#29362: *143060 FastCGI sent in stderr: "Primary script unknown" while reading response header from upstream, client: 192.168.1.100, server: , request: "GET /plugins/dynamix.my.servers/include/state.php HTTP/2.0", upstream: "fastcgi://unix:/var/run/php5-fpm.sock:", host: "xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx.unraid.net", referrer: "https://xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx.unraid.net/Dashboard"
-
Correct way to move files between shares?
When copying files from one share to another share via an intermediate Windows10 VM is the virtual network connection a limiting factor? I get max 500-600mbps (about 50-75MB/s) when copying large files. Is the limit the HDDs or the virtual network?
-
[Plugin] NUT v2 - Network UPS Tools
I have just noticed, following a short (few seconds) power outage that there is no UPS failure notification/event in the log file. When using the built-in unRAID UPS support it used to catch them all. Also, can UPS events (power failures) be marked as Error/Warning/System in the log file?
-
Home assistant
I tried it on Docker but then opted for the VM path - wanted the whole HASS.IO package benefits. Runs very stable. Did you try it on a VM in unRAID or do you have a reason not to run it on a VM in unraid? Do you take down or restart your unRAID often?
-
[Support] Linuxserver.io - Qbittorrent
I also have the same problem - new Qbittorrent docker user (used until now on my Win10 VM with no issues)
-
[Support] Linuxserver.io - Qbittorrent
OK I misread the original fix post. I recreated just the WEBUI port, but did not create an additional WEBUI parameter. Now working THX
-
[Support] Linuxserver.io - Qbittorrent
I have tried changing the default port as mentioned in this thread - with NO success My Docker configuration: Docker Command: I tried manually going to port 192.168.1.104:8083 but always get "This site canโt be reached" error All my other dockers WEBUI work OK. What I noticed is that the qBittorent.conf file has the following parameter: WebUI\Port=8080 even when I change it or completely delete the file or the whole Docker appdata folder each time I run the docker it is recreated with the 8080 port. I tried reinstalling the docker a few time with the port change but still not working. How can I get it working?
-
MACRIUM REFLECT mrimg to VM?
Looking for an answer to this a well
-
Unraid 14th Birthday Case Badge Giveaway
Have been a paid user for almost 9 years (2010). The best thing I like about unRAID is that I forget it is there ๐ although I like tinkering I only need to when I want and have time and not when the server asks for help - which it doesn't !!! Keep up the wonderful work.
-
VirtualBox Plugin for unRAID v5 and v6
I have tried compiling for 6.4 and am having compilation problems... will continue to try.
-
Server Layout Plugin for unRAID v6
Sorry for the delay. I have other things on my plate at the moment. Released update. 2018.01.25 - Updated for unRAID v6.4 - Thank you Squid