maxse Posted October 11, 2021 Share Posted October 11, 2021 Hi folks, I need some help, not sure if this is the correct subforum, please feel free to move it is not. I started having an issue with my remote unraid server reporting that the APC1001 Pro (600W) backup power supply is always on "low battery status" I'm not sure when this issue started happening. I have never had an issue with 3 units over may years that I've owned this exact APC backup. I did purchased it used, and originally bought a new battery for it. When I started seeing unraid report low battery and a runtime of only 1-2 minutes, I bought a new battery, and I'm having the same issue! This does not happen with my main unraid server where I have had a new battery for 2-3 years even. Any idea of what is causing this? Could it be the actual unit breaking, as opposed to a battery? Remember, this is a brand new battery that I just installed into it. I would imagine if the unit was going dead it would simply not power on instead of reporting low battery even though the battery is brand new and the other battery in it was only 1 year old. The load on the UPS is only 33% ~200 watts. Any ideas? POWER UPS Load: 25.0 % - 150 Watts UPS status:Online LOWBATT Battery charge:100.0 Percent Runtime left:1.9 Minutes Nominal power:600 Watts Quote Link to comment
ChatNoir Posted October 11, 2021 Share Posted October 11, 2021 When you replaced the battery, did you just put it in the unit and called it a day ? If so, it is possible that the APC firmware still consider the battery as "old". I had a similar problem and I had to plug the USB of the UPS in a windows machine, install a dedicated APC software, update the install date of the battery and run some test on it. After that it was OK. 1 Quote Link to comment
wildfire305 Posted October 12, 2021 Share Posted October 12, 2021 Agreed. I have also had to tell my apc I replaced that battery using the windows app. Quote Link to comment
maxse Posted October 12, 2021 Author Share Posted October 12, 2021 Oh wow. Thank you so much folks! yes, I just went ahead and popped it in. Anyone know if this could be done in Linux? I have this installed in a remote location and it would be difficult. Is there anything in Unraid that can do this? I guess worst case is I could look into installed a windows VM? But then how would I pass it through to the windows machine? Quote Link to comment
S80_UK Posted October 13, 2021 Share Posted October 13, 2021 (edited) I posted about this a while ago... Have a read of that thread. The suggested method that I give there for recalibrating the UPS settings for a replaced battery is probably what you need. This can all be done from Unraid via a command line window or ssh session for example. Edited October 13, 2021 by S80_UK 1 Quote Link to comment
maxse Posted October 21, 2021 Author Share Posted October 21, 2021 (edited) WOW, thank you sooo much! It worked! I had to update the date of the battery but it worked. You guys are THE BEST. I love this community! Thank again! Edited October 21, 2021 by maxse 1 Quote Link to comment