V6 Plugin for APC UPS


mr_cb7

Recommended Posts

Has anyone seen odd issues with the built in one?

I have not had issues with the v5 APC UPS driver - the v6 one seems to always display around 0.76 minutes to 2.25 minutes left.

 

It is a APC UPS backup-pro 750, 27% load and on v5 42minute runtime. all other stats are as before.

In one case unraid shutdown based on the UPS state.

 

Right now I have the runtime setting set to 0 in hopes it disables that check.

 

Link to comment

Has anyone seen odd issues with the built in one?

I have not had issues with the v5 APC UPS driver - the v6 one seems to always display around 0.76 minutes to 2.25 minutes left.

How old is your battery? Typical life is between 2-4 years, but sometimes less. A cell gone bad in the UPS battery will severely cut down runtime, and the UPS is able to sense that.
Link to comment
  • 4 weeks later...

Think may have this one solved. It appears to be a APC UPS issue. Around the same time as my v5 -> v6 upgrade I swapped a new battery in. In some cases the APC will have a brain fart and get confused. Under windows the APC app would do a calibration, for apcupd a manual calibration is required.

 

I just swapped it with another APC unit I had and it works fine now

 

Link to comment