November 26, 201510 yr I just picked up a Back-Ups 550 UPS, and got most of the stats automatically it needs, except for the LoadPCT. Has anyone else run into this issue with the UPS app in 6.1.4?
January 29, 201610 yr Yes, I just installed the same UPS today and I too do not get a "UPS Load" or "Nominal Power". I do however show the UPS Load %
January 29, 201610 yr Community Expert exact same situation and UPS on dashboard i get battery charge 100% runtime left 74 minutes (seems too high) nominal power - UPS load - UPS Load % 9.0 percent
February 5, 201610 yr Author There's another thread here that is dealing with the same issue(s) http://lime-technology.com/forum/index.php?topic=45088.new;topicseen#new
February 5, 201610 yr Mine does this too. I think it's because this is a lower end UPS. 550 x 0.09 = 49.5w Easy enough to calculate no?
February 5, 201610 yr Mine does this too. I think it's because this is a lower end UPS. 550 x 0.09 = 49.5w Easy enough to calculate no? Except that the 550 is not the wattage rating. It's the Volt-Amps rating. That particular UPS is only rated to 330 watts. 330 * .09 = 29.7 watts. More info here if you're interested: http://www.power-solutions.com/watts-va