mrmarkfr Posted November 26, 2015 Share Posted November 26, 2015 I just picked up a Back-Ups 550 UPS, and got most of the stats automatically it needs, except for the LoadPCT. Has anyone else run into this issue with the UPS app in 6.1.4? Link to comment
sport Posted January 29, 2016 Share Posted January 29, 2016 Yes, I just installed the same UPS today and I too do not get a "UPS Load" or "Nominal Power". I do however show the UPS Load % Link to comment
grither Posted January 29, 2016 Share Posted January 29, 2016 exact same situation and UPS on dashboard i get battery charge 100% runtime left 74 minutes (seems too high) nominal power - UPS load - UPS Load % 9.0 percent Link to comment
mrmarkfr Posted February 5, 2016 Author Share Posted February 5, 2016 There's another thread here that is dealing with the same issue(s) http://lime-technology.com/forum/index.php?topic=45088.new;topicseen#new Link to comment
mr-hexen Posted February 5, 2016 Share Posted February 5, 2016 Mine does this too. I think it's because this is a lower end UPS. 550 x 0.09 = 49.5w Easy enough to calculate no? Link to comment
Matt_G Posted February 5, 2016 Share Posted February 5, 2016 Mine does this too. I think it's because this is a lower end UPS. 550 x 0.09 = 49.5w Easy enough to calculate no? Except that the 550 is not the wattage rating. It's the Volt-Amps rating. That particular UPS is only rated to 330 watts. 330 * .09 = 29.7 watts. More info here if you're interested: http://www.power-solutions.com/watts-va Link to comment