[Plugin] NUT v2 - Network UPS Tools

Featured Replies

I built latest nut sources for unRAID with usb support only.

 

Here is steps to build it on ubuntu/debian:

 

apt update && apt install ca-certificates freeipmi git libusb-dev autoconf automake make libtool python --no-install-recommends -y
git clone --depth 1  https://github.com/networkupstools/nut.git && cd nut
./autogen.sh
./configure --enable-strip --with-usb --datarootdir=/usr/share/nut --bindir=/usr/bin --sbindir=/usr/sbin --prefix=/ --sysconfdir=/etc/nut --libexecdir=/usr/libexec/nut --runstatedir=/var/run/nut --libdir=/usr/lib64 --with-drvpath=/usr/libexec/nut && make -j `nproc` &&  make install


 

 

 

Edited by IGHOR

  • Replies 2.1k
  • Views 457.6k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • I am stopping updates for my version of the plugin. Update to the latest version 2023.09.17 and then you can remove my version and install Rysz's from CA and it will retain your configs.   T

  • Released 2023.07.26, @ich777 is creating a new package for me to use, and I want to look to move to 2.8 as the default version but will need to check upgrade path works ok.

  • That APC BX series is known to suffer from this (what we believe to be) firmware issue and we've put patches in place to suppress this unwanted behaviour on the UPS side. Here's how you can set it up:

Posted Images

3 minutes ago, IGHOR said:

I built latest nut sources for unRAID with usb support only.

In terminal tests it works fine, I'm getting outputs of voltages, but in unRAID UI it won't display info.

Anyone how to fix it?

 

Here is steps to build it on ubuntu/debian:

 



apt update && apt install ca-certificates freeipmi git libusb-dev autoconf automake make libtool python --no-install-recommends -y
git clone --depth 1  https://github.com/networkupstools/nut.git && cd nut
./autogen.sh
./configure --enable-strip --with-usb --datarootdir=/usr/share/nut --bindir=/usr/bin --sbindir=/usr/sbin --prefix=/ --sysconfdir=/etc/nut --libexecdir=/usr/libexec/nut --libdir=/usr/lib64 --with-drvpath=/usr/libexec/nut && make -j `nproc` &&  make install


 

 

nut-2.7.4.1.20210620-x86_64-1.txz 805.54 kB · 0 downloads

It was recommended to me on unraid subreddit to spin up an Ubuntu VM. Pass through the usb connection and make it the host. Then make unraid NUT the slave and it would read the host. 
 

wish the plugin maker would reply or update this flipping build. 
 

No idea on that either. 

Edited by Jammy B

20 minutes ago, Jammy B said:

wish the plugin maker would reply or update this flipping build. 

Actually latest compilation of nut is working. It is possible parsing problem in the plugin code, not nut itself
In command line it works

root@unRAID:/# upsc [email protected]
battery.voltage: 27.30
device.type: ups
driver.flag.noscanlangid: enabled
driver.flag.novendor: enabled
driver.name: nutdrv_qx
driver.parameter.langid_fix: 0x0409
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0000
driver.parameter.protocol: hunnox
driver.parameter.synchronous: no
driver.parameter.vendorid: 0001
driver.version: 2.7.4.1
driver.version.data: Hunnox 0.01
driver.version.internal: 0.30
input.frequency: 49.6
input.voltage: 217.0
input.voltage.fault: 0.0
output.voltage: 220.0
ups.beeper.status: disabled
ups.delay.shutdown: 60
ups.delay.start: 0
ups.load: 13
ups.productid: 0000
ups.status: OL
ups.temperature: 29.0
ups.type: offline / line interactive
ups.vendorid: 0001

 

Edited by IGHOR

I fixed it, maybe it is just enough to put the file to this folder /boot/config/plugins/nut

Or replace existing one. Anyway if extracted to root, it starts working instantly.

 

So everything is working fine with nut compiled from latest sources.

There should be nothing that stops plugin dev to release an update.

Here is a right commands to compile nut to run on unRAID:

apt update && apt install ca-certificates freeipmi git libusb-dev autoconf automake make libtool python --no-install-recommends -y
git clone --depth 1  https://github.com/networkupstools/nut.git && cd nut
./autogen.sh

./configure --enable-strip --runstatedir=/var/run/nut --with-pidpath=/var/run/nut --with-usb --datarootdir=/usr/share/nut --bindir=/usr/bin --sbindir=/usr/sbin --prefix=/ --sysconfdir=/etc/nut --libexecdir=/usr/libexec/nut --libdir=/usr/lib64 --with-drvpath=/usr/libexec/nut && make -j `nproc` &&  make install

 

nut-2.7.4.1.20210620-x86_64-1.txz

Edited by IGHOR

@IGHOR 

 

Can I be really cheeky and ask that you make a step-by-step guide to do all this please?

 

would love to update NUT and get my Powercool working. 
 

edit. To add, it’ll make all of us who to update it and add more UPSs to it a lot more willing!

 

 

. 👍

Edited by Jammy B

1 hour ago, Jammy B said:

@IGHOR 

 

Can I be really cheeky and ask that you make a step-by-step guide to do all this please?

 

 

I think you need just copy the file 'nut-2.7.4.1.20210620-x86_64-1.txz' attached in my message to folder /boot/config/plugins/nut
And reboot server, it may use latest version of nut instead of old one.

If it not works this way, replace existing nut-2.7.4... file in folder /boot/config/plugins/nut by my file and reboot

I tested and it survived reboot, also here is updated file with some fixes.

How to install:

1) copy the attached file and replace it in the folder /boot/config/plugins/nut

2) reboot

It will remain to be the same plugin, but with newer nut v2.7.4.1 for usb devices only.

Once plugin dev update it officially, it will be upgraded natively

nut-2.7.4.20200318-x86_64-1.txz

@IGHOR

 

YOU ARE THE MAN!!!!!!

 

powered down my unraid system.

 

removed usb key

 

plugged into laptop and copied your file over.

 

back into machine, boot up and autodetect set custom driver.

 

it flippin' works! whilst i don't get

BATTERY CHARGE %

RUNTIME LEFT

NOMINAL POWER

UPS LOAD

 

i do get UPS LOAD % 

 

when i kill power to the UPS, unraid knows about it! i've set it to power down the system after 4 minutes of battery time. when i turn power back on, the unraid recognises it is!

 

all telegram notifications work as well.

 

thank you so much for doing this!

1 hour ago, Jammy B said:

i don't get

BATTERY CHARGE %

RUNTIME LEFT

NOMINAL POWER

UPS LOAD

 

I think nut can't get those values from some UPS
And driver calculate it by voltage, and if you calibrate nut and define high/low voltages it will show % and runtime left

3 minutes ago, IGHOR said:

 

I think nut can't get those values from some UPS
And driver calculate it by voltage, and if you calibrate nut and define high/low voltages it will show % and runtime left


How would I go about calibrating NUT?

57 minutes ago, Jammy B said:


How would I go about calibrating NUT?

You need to find out those values for your ups
default.battery.voltage.high =
default.battery.voltage.low =
default.battery.voltage.nominal =

You’re right. The manual only shows 12v. But typically if you post something inaccurate, you get helpful responses. 👍

 

see attached screenshots of NUT which don’t show a lot either. 
 

so based on your link. 
 

high = 13v

nominal = 12v

low = 10.7v

 

although NUT says battery voltage 27.10? So the batteries in series?

 

so high = 27.10v

nominal = 24v

low = 21.4v


 

3A7EEA5F-BDEC-487A-82D0-19699AA73EFB.jpeg

754759B1-42BF-44F4-91BA-FEF014A23274.jpeg

Edited by Jammy B

17 hours ago, IGHOR said:

You need to find out those values for your ups
default.battery.voltage.high =
default.battery.voltage.low =
default.battery.voltage.nominal =

 

so i've put these values into ups.conf and its now showing 100% battery on status.

 

so high = 27.50v [NUT says that that is current battery voltage now]

nominal = 24v

low = 21.4v

 

how do i go about doing a calibration? do i literally kill the power and watch the % drop?

2 hours ago, Jammy B said:

do i literally kill the power and watch the % drop?

Yes, but with the server getting power from a different source so it stays running. Put a load roughly equivalent to the server on the UPS output, and turn off the power feeding the UPS but not the server (obviously).

You may need to tweak the battery voltage low value to match what value actually shows up in NUT a few seconds before the UPS shuts itself down from low battery. Once the UPS shuts itself off, turn the power back on with the dummy load running and time how long it takes to return the battery to voltage high so you know the recharge rate.

During this testing, make sure NUT is configured NOT to shut down the server.

11 minutes ago, jonathanm said:

Yes, but with the server getting power from a different source so it stays running. Put a load roughly equivalent to the server on the UPS output, and turn off the power feeding the UPS but not the server (obviously).

You may need to tweak the battery voltage low value to match what value actually shows up in NUT a few seconds before the UPS shuts itself down from low battery. Once the UPS shuts itself off, turn the power back on with the dummy load running and time how long it takes to return the battery to voltage high so you know the recharge rate.

During this testing, make sure NUT is configured NOT to shut down the server.

got you.

 

will give this a whirl at the weekend. thanks for the help.

 

 

How often does NUT poll the battery voltage?

 

after setting the high/nominal/low values. If I refresh the page the charge jumps between 97% to 100%
 

do I need to set a polling time?

On 6/24/2021 at 4:32 PM, IGHOR said:

You need to find out those values for your ups
default.battery.voltage.high =
default.battery.voltage.low =
default.battery.voltage.nominal =


 

having an issue making the above settings persist in ups.conf

 

as you can see below. It’s disappeared. 
 

how do I keep them in the ups.conf file?

 

all works when in battery mode. 
 

edit

nothing works until I put it all back in. 

1C8A1C93-43C1-4370-BC80-5870B400B275.jpeg

Edited by Jammy B

8 minutes ago, Jammy B said:

as you can see below. It’s disappeared

You need to use manual config only

image.thumb.png.a7f6fab64283768ab7954b31738c2e2c.png

1 hour ago, IGHOR said:

You need to use manual config only

image.thumb.png.a7f6fab64283768ab7954b31738c2e2c.png

 

ahh

image.png.1a606ef1a623c72ba444def7ab7d7ba2.png

 

 

every days a school day.

 

will re-edit my ups.conf file and make sure its enabled.

 

thanks for the advice @IGHOR as always,.

 

hi, I just get used to Unraid and installed the NUT plugin. I was wondering about the red "w":

306624537_Bildschirmfoto2021-06-28um13_10_34.thumb.png.6fb7243e7bc53e7a67b8e6172c3073d2.png

 

any hints how to get it working without any red warning signs? ;)

 

In Addition here are the automatically detected details of my APS UPS:

1903180557_Bildschirmfoto2021-06-28um13_10_16.thumb.png.eb6125fb39d90dc30285664783515e3c.png

FWIW: I have this item in RED since years...never worried about it.

2 hours ago, nicx said:

hi, I just get used to Unraid and installed the NUT plugin. I was wondering about the red "w":

306624537_Bildschirmfoto2021-06-28um13_10_34.thumb.png.6fb7243e7bc53e7a67b8e6172c3073d2.png

 

any hints how to get it working without any red warning signs? ;)

 

In Addition here are the automatically detected details of my APS UPS:

1903180557_Bildschirmfoto2021-06-28um13_10_16.thumb.png.eb6125fb39d90dc30285664783515e3c.png

Is there any reason why you’re using NUT instead of the built in UPS manager in unraid?

 

APC works great with the built in one. It’s a couple items to the right of NUT settings. 

19 minutes ago, Jammy B said:

Is there any reason why you’re using NUT instead of the built in UPS manager in unraid?

 

APC works great with the built in one. It’s a couple items to the right of NUT settings. 

I am using NUT because I need network access to the NUT server. And as far as I understand the integrated UPS manager is not able to do that.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.