Woogz Posted April 12, 2022 Share Posted April 12, 2022 I've got a specific use case I'm hoping someone can help me solve. I want my unRAID server and a NUT client to automatically power on when AC power is restored to my UPS but I can't have Nut turn my UPS off when unRAID and my client shutdown because I have a USB device that needs to remain powered for as long as I can manage otherwise it needs manual intervention. Is there a way to accomplish what I'm asking for? Quote Link to comment
Anym001 Posted April 29, 2022 Share Posted April 29, 2022 Hello, recently the following error messages appear more often in the syslog. usbhid-ups[3717]: nut_libusb_get_string: Pipe error. The UPS (Cyberpower CP900EPFCLCD) still works without problems. Unfortunately I can't find anything on google about this issue. Anyone have an idea what this is all about? Quote Link to comment
dmot7291 Posted May 8, 2022 Share Posted May 8, 2022 (edited) Edit: 2022-05-09 I found the issue, running upsmon gave the following Network UPS Tools upsmon 2.7.4.1 fopen /var/run/nut/upsmon.pid: No such file or directory Unable to use old-style MONITOR line without a username Convert it and add a username to upsd.users - see the documentation Fatal error: unusable configuration which isn't particularly helpful. I changed the password to one without any special characters just [A-Za-z0-9] and the plugin works as expected. Leaving this here in case anyone else stumbled across this as the logging for NUT and its tools wasn't helpful when the issue was simply an incorrect password. Hey, having trouble getting the plugin to connect to my UPS and I've no idea what's wrong. The UPS is a CP1500EPFCLCD (https://networkupstools.org/ddl/Cyber_Power_Systems/CP1500EPFCLCD.html) These are the settings: /var/log/syslog shows May 9 00:08:03 plex-server ool www[14337]: /usr/local/emhttp/plugins/nut/scripts/start May 9 00:08:05 plex-server usbhid-ups[15659]: Startup successful May 9 00:08:06 plex-server upsd[15666]: listening on 0.0.0.0 port 3493 May 9 00:08:06 plex-server upsd[15666]: Connected to UPS [ups]: usbhid-ups-ups May 9 00:08:06 plex-server upsd[15667]: Startup successful but the plugin just shows Status: Stopped Can anyone help? Fairly certain it's working correctly, running: upsc [email protected]:3493 battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 4890 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 24.0 battery.voltage.nominal: 24 device.mfr: CPS device.model: CP1500EPFCLCD device.serial: CRXLW2000017 device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: no driver.version: 2.7.4.1 driver.version.data: CyberPower HID 0.5 driver.version.internal: 0.55 driver.version.usb: libusb-1.0.23 (API: 0x1000107) input.transfer.high: 260 input.transfer.low: 170 input.voltage: 239.0 input.voltage.nominal: 230 output.voltage: 260.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 9 ups.mfr: CPS ups.model: CP1500EPFCLCD ups.productid: 0501 ups.realpower.nominal: 900 ups.serial: CRXLW2000017 ups.status: OL ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 and I can configure collectd and get metrics: <Plugin nut> UPS "[email protected]:3493" </Plugin> Edited May 9, 2022 by dmot7291 Quote Link to comment
sailingbikeruk Posted May 29, 2022 Share Posted May 29, 2022 (edited) Does anybody have this working as a NUT server? I have the plugin working and it is showing the UPS stats, it also gives me the Slave username and password, but I cant get WinNUT Client to connect at all. UPS type is set to NetServer NMAP shows the port (3493) is open and the service is nut The WINNut Client is configured to use the Unraid Server IP and the port 3493 I've allowed the Client throgh the windows firewall (i've even tried disabling it) I've tried all the user/password combinations but it doesn't connect at all. Any suggestions? Edited May 29, 2022 by sailingbikeruk duplicated images Quote Link to comment
Vr2Io Posted May 30, 2022 Share Posted May 30, 2022 8 hours ago, sailingbikeruk said: Does anybody have this working as a NUT server? I have the plugin working and it is showing the UPS stats, it also gives me the Slave username and password, but I cant get WinNUT Client to connect at all. UPS type is set to NetServer NMAP shows the port (3493) is open and the service is nut The WINNut Client is configured to use the Unraid Server IP and the port 3493 I've allowed the Client throgh the windows firewall (i've even tried disabling it) I've tried all the user/password combinations but it doesn't connect at all. Any suggestions? There are different version "WinNUT" https://networkupstools.org/projects.html#_a_href_http_sourceforge_net_projects_winnutclient_windows_nut_client_a I share the UPS ( netserver ) to HA, Unraid, NAS fine, if possible, try to setup a trial Unraid as client to verify may be an easy way. Quote Link to comment
sailingbikeruk Posted May 30, 2022 Share Posted May 30, 2022 5 hours ago, Vr2Io said: There are different version "WinNUT" https://networkupstools.org/projects.html#_a_href_http_sourceforge_net_projects_winnutclient_windows_nut_client_a I share the UPS ( netserver ) to HA, Unraid, NAS fine, if possible, try to setup a trial Unraid as client to verify may be an easy way. I have V2 from https://github.com/gawindx/WinNUT-Client Are you using NUT on Unraid as the Server or is that a client with the NUT Server somewhere else? I'll try as you suggest and see if I an get it to work Quote Link to comment
UBS Posted May 30, 2022 Share Posted May 30, 2022 1 hour ago, sailingbikeruk said: I have V2 from https://github.com/gawindx/WinNUT-Client Are you using NUT on Unraid as the Server or is that a client with the NUT Server somewhere else? I'll try as you suggest and see if I an get it to work try to fill [email protected] format in address Quote Link to comment
Vr2Io Posted May 30, 2022 Share Posted May 30, 2022 (edited) 1 hour ago, sailingbikeruk said: Are you using NUT on Unraid as the Server Of course, another Unraid as client and access by different client for longtime. Edited May 30, 2022 by Vr2Io Quote Link to comment
sailingbikeruk Posted May 30, 2022 Share Posted May 30, 2022 (edited) 3 hours ago, Vr2Io said: Of course, another Unraid as client and access by different client for longtime. Ok... I'll dig out an old laptop and make a new USB and see if I can get the two to talk to each other. EDIT: I've done this and it connected straight away so the issue must be with the windows client or connectivity. Thanks for the suggestion, i'll do some more trouble shooting on windows. EDIT: This is now working... I am embarassed to tell you what the issue was as it is so damn stupid, but for others, just in case, I had not set a polling interval, the default in settings is 0. Thanks for everyones help Edited May 30, 2022 by sailingbikeruk Quote Link to comment
Siridar Posted June 7, 2022 Share Posted June 7, 2022 (edited) @dmacias Can we expect newer version soon including 'nutdrv_qx/armac' subdriver. Or maybe anyone knows how can I install one manually? Edited June 7, 2022 by Siridar Quote Link to comment
TeroS Posted June 19, 2022 Share Posted June 19, 2022 Minor thing but still, the "w" should be "W" for power, the same is in dashboard: Quote Link to comment
johnmick Posted June 21, 2022 Share Posted June 21, 2022 (edited) Is there any way to send the NUT data out through mqtt? I'm trying to add the UPS energy data to homeassistant. I've tried the NUT intergration in homeassistant, but here's all I get: Battery Charge 100 % Input Voltage 239.0 V Load 11 % Status Online How should I acquire the energy data? Edited June 23, 2022 by johnmick Quote Link to comment
a24425311 Posted July 1, 2022 Share Posted July 1, 2022 (edited) I have been using NUT plugin since it launched (slave, master was my Syno server), it was running very fine until recently I upgraded my unraid rig, it gives me an immediate auto 90 sec shutdown after powering up, shutdown load was set at 20% and my load was still 100%/30+ mins, any thoughts? Thanks for reading. 05/July Little update, i solved the problem by resetting the UPS breaker (arent so sure if it was caused by the breaker but just work.) Edited July 5, 2022 by a24425311 Quote Link to comment
Capt.Insano Posted July 3, 2022 Share Posted July 3, 2022 @dmacias Firstly, thanks so much for your work on this! Secondly (cheekily!), any chance of an update to this plugin? A new official release of NUT has been released (v2.8.0) and among other things, it happens to include a fix an issue with my UPS!! https://github.com/networkupstools/nut/releases/tag/v2.8.0 Thanks again! Quote Link to comment
MoherPower Posted July 25, 2022 Share Posted July 25, 2022 I have problem with ups Power off. I want my unraid to power off itself immediately when main power fails. that is why i set it to Shutdown Mode: Battery Level Battery Runtime Left: Battery Runtime Battery level to initiate shutdown (%): 96 UPS Mode: Standalone Turn off UPS after shutdown: NO Unraid start shutdown 30sec after power failure but it also turns OFF UPS. this leads to parity check and to powering off all my network switches and stuff. It also leaves my UPS in strange state that even after returning main power needs me to push the powerbutton on UPS to start working. This is not happening when my UPS runs ouf of battery. After power returns it just turns on. My ups is PowerWalker VI 850 LCD Can you help me to solve this problem? Quote Link to comment
grizzly Posted July 25, 2022 Share Posted July 25, 2022 I´m pretty sure i read something about to short % or time can cause problems. And also that it can work for a while but then when batteries wear down starts to cause problems. But i´m not 100% sure about this, i can have it mixed up with something else and it was a few years ago. And i think i did have some problem with using a high % on my last ups many years ago, that i solved by using time instead. Since then i have used shut down after 3min and it has worked fine chosed 3min because when power come back here it almost always shuts of again after 10-20sec and come back after 5sec 3-4 times before it stabilize. So try a lower % or try time instead and maybe not to low of a time. And remember when trying this do not have unraid power in the ups (only USB cable). Connect the power to a regular outlet so IF the ups cuts power to early you won´t get a unclean shutdown and a parity check. As long as you connect the USB cable unraid and ups will talk to each other normally and will initiate a shutdown when you yank the cable or use a on/off switch, so just look/listening for when unraid shut off and see if ups turn of before that or not. Quote Link to comment
pyrlix Posted July 25, 2022 Share Posted July 25, 2022 I have something exotic here it seems I recently acquired a Vertiv Liebert GXT5-1500 for my Servercloset, and i am happy with it sofar. However i cant seem to get it to work with NUT at all. It wont find it with the USBHID driver, always complains about no device being found. I tried to set various ports and tried various drivers with no result. Interestingly, in a way, the GXT5s USB Port acts as both a HID and CDC device. THe Unit reports both a ttyACM0 aswell as a hid-generic device. Maybe i am doing something wrong aswell, but i am not awawre what it could be. Quote Link to comment
YrDaDy Posted August 5, 2022 Share Posted August 5, 2022 On 7/25/2022 at 12:09 PM, pyrlix said: I have something exotic here it seems I recently acquired a Vertiv Liebert GXT5-1500 for my Servercloset, and i am happy with it sofar. However i cant seem to get it to work with NUT at all. It wont find it with the USBHID driver, always complains about no device being found. I tried to set various ports and tried various drivers with no result. Interestingly, in a way, the GXT5s USB Port acts as both a HID and CDC device. THe Unit reports both a ttyACM0 aswell as a hid-generic device. Maybe i am doing something wrong aswell, but i am not awawre what it could be. Ironically, I just grabbed the exact same thing and having the same issue. Any luck? Quote Link to comment
xsweb Posted August 7, 2022 Share Posted August 7, 2022 hi Recently I noted a bit of a strange behavior with the consuming display in the status bar. If the UPS load is below a certain % of usage, it shows the (calculated) wattages. But when it's getting over this value, it only shows 1w for the current consumption. The dashboard it self show always the (calculated) wattages. Unraid Version: 6.10.3 UPS: PowerWalker VI 1200 SHL (1200VA/600W) Quote Link to comment
Sleepyme Posted August 12, 2022 Share Posted August 12, 2022 Can individual plugs be turned off after computer shuts down? Quote Link to comment
Batman Posted August 19, 2022 Share Posted August 19, 2022 On 2/15/2022 at 1:53 AM, s1oz said: Lost UPS after running for a while, NUT plugin shows running, but no UPS device shows After re-plugging and unplugging the USB, restart the NUT plugin and enable it normally Feb 1 11:03:10 Tower upsmon[14759]: Poll UPS [[email protected]] failed - Data stale Feb 1 11:03:11 Tower usbhid-ups[13944]: device->Product is NULL so it is not possible to determine whether to activate max_report_size workaround Feb 1 11:03:13 Tower usbhid-ups[13944]: device->Product is NULL so it is not possible to determine whether to activate max_report_size workaround Feb 1 11:03:15 Tower usbhid-ups[13944]: device->Product is NULL so it is not possible to determine whether to activate max_report_size workaround Feb 1 11:03:15 Tower upsmon[14759]: Poll UPS [[email protected]] failed - Data stale Feb 1 11:03:17 Tower usbhid-ups[13944]: device->Product is NULL so it is not possible to determine whether to activate max_report_size workaround Feb 1 11:03:19 Tower usbhid-ups[13944]: device->Product is NULL so it is not possible to determine whether to activate max_report_size workaround I'm getting the same error message every few days. It doesn't seem to correlate to a particular time or event. Unraid's built-in UPS tool never had these dropouts, but I switched to NUT because APCUPSD interpreted the fully-charged state of my UPS as a power failure (my UPS was reporting "Online + On Battery"). I have an APC BGM1500B. When I unplug and replug the UPS into the server, it works again after restarting NUT. Restarting NUT, or disabling and reenabling without unplugging the USB cable does not fix the problem. Quote Link to comment
k1netic Posted August 19, 2022 Share Posted August 19, 2022 (edited) Hey everyone, Ive been doing my head in trying to get a ups to play nice with nut, but it seems ive hit a wall and cant sort it out myself. At the moment i can detect it and connect, but get no information from it and the server is unaware when the ups switches to battery mode. I am fairly certain i need to use subdriver and/or protocol hunnox to get my device to work. it looks like @IGHOR may have had the answer in the form of a modified .txz file to help out @Jammy B but that link is no longer available. Info below to ID my unit, its a Digitech MP-5205 650VA but seems to be a clone of powercool, or maybe the other way around... Scanning for UPS... [nutdev1] driver = "nutdrv_qx" port = "auto" vendorid = "0001" productid = "0000" product = "MEC0003" bus = "002" /etc/nut/ups.conf [ups] driver = nutdrv_qx port = auto subdriver = hunnox vendorid = 0001 productid = 0000 langid_fix = 0x0409 novendor ondelay = 180 offdelay = 60 default.battery.voltage.high = 13 default.battery.voltage.low = 11 default.battery.voltage.nominal = 12.7 override.battery.packs = 6 runtimecal = 480,100,1200,50 chargetime = 28800 [email protected]:~# upsdrvctl start Network UPS Tools - UPS driver controller 2.7.4.1 Network UPS Tools - Generic Q* USB/Serial driver 0.39 (2.7.4.1) USB communication driver 0.43 Subdriver 'hunnox' not found! Driver failed to start (exit status=1) If i remove the subdriver line from ups.conf i can get this [email protected]:~# upsc [email protected] battery.charge: 1 battery.packs: 6 battery.runtime: 37 battery.voltage: 0.00 battery.voltage.high: 13 battery.voltage.low: 11 battery.voltage.nominal: 12.7 device.type: ups driver.name: nutdrv_qx driver.parameter.chargetime: 28800 driver.parameter.offdelay: 60 driver.parameter.ondelay: 180 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.productid: 0000 driver.parameter.runtimecal: 480,100,1200,50 driver.parameter.synchronous: no driver.parameter.vendorid: 0001 driver.version: 2.7.4.1 driver.version.data: Q1 0.07 driver.version.internal: 0.39 driver.version.usb: libusb-1.0.24 (API: 0x1000107) input.frequency: 0.0 input.voltage: 0.0 input.voltage.fault: 0.0 output.voltage: 0.0 ups.beeper.status: disabled ups.delay.shutdown: 60 ups.delay.start: 180 ups.load: 0 ups.productid: 0000 ups.status: OL ups.temperature: 0.0 ups.type: online ups.vendorid: 0001 I tried compiling from git in ubuntu but its a bit out of my league for the moment. Cheers Edited August 19, 2022 by k1netic spelling Quote Link to comment
Batman Posted August 20, 2022 Share Posted August 20, 2022 (edited) On 8/18/2022 at 7:50 PM, Batman said: I'm getting the same error message every few days. It doesn't seem to correlate to a particular time or event. Unraid's built-in UPS tool never had these dropouts, but I switched to NUT because APCUPSD interpreted the fully-charged state of my UPS as a power failure (my UPS was reporting "Online + On Battery"). I have an APC BGM1500B. When I unplug and replug the UPS into the server, it works again after restarting NUT. Restarting NUT, or disabling and reenabling without unplugging the USB cable does not fix the problem. It would be nice to actually solve the issue, but I wrote a short script that resets the USB when the connection is lost. It's scheduled to run on a regular basis with the User Scripts plugin. #!/bin/bash # Test communication with UPS if upscmd -l ups > /dev/nul; then echo The UPS is connected. else echo Error: Communication with the UPS has failed! if usbreset "Back-UPS BGM1500 FW:000000G0-313200S9"; then echo USB reset completed successfully. else echo Error: USB reset failed! fi fi Edit: usbreset now shows a slightly different name for my UPS, so the script above stopped working. I couldn't figure out if or how usbreset would use wildcards, so this modified script works: #!/bin/bash # Test communication with UPS if upscmd -l ups > /dev/nul; then echo The UPS is connected. else echo Error: Communication with the UPS has failed! # Get USB path for the UPS APC=$( lsusb | grep "American Power Conversion" | perl -nE "/\D+(\d+)\D+(\d+).+/; print qq(\$1/\$2)") # Test for a USB conection if [ -z "$APC" ]; then echo Error: No USB UPS detected! else echo Resetting the USB connection... # Reset the USB connection if usbreset $APC; then echo USB reset completed successfully. else echo Error: USB reset failed! fi fi fi Edited August 20, 2022 by Batman 1 Quote Link to comment
k1netic Posted August 20, 2022 Share Posted August 20, 2022 19 hours ago, k1netic said: Hey everyone, Ive been doing my head in trying to get a ups to play nice with nut, but it seems ive hit a wall and cant sort it out myself. At the moment i can detect it and connect, but get no information from it and the server is unaware when the ups switches to battery mode. I am fairly certain i need to use subdriver and/or protocol hunnox to get my device to work. it looks like @IGHOR may have had the answer in the form of a modified .txz file to help out @Jammy B but that link is no longer available. Info below to ID my unit, its a Digitech MP-5205 650VA but seems to be a clone of powercool, or maybe the other way around... Scanning for UPS... [nutdev1] driver = "nutdrv_qx" port = "auto" vendorid = "0001" productid = "0000" product = "MEC0003" bus = "002" /etc/nut/ups.conf [ups] driver = nutdrv_qx port = auto subdriver = hunnox vendorid = 0001 productid = 0000 langid_fix = 0x0409 novendor ondelay = 180 offdelay = 60 default.battery.voltage.high = 13 default.battery.voltage.low = 11 default.battery.voltage.nominal = 12.7 override.battery.packs = 6 runtimecal = 480,100,1200,50 chargetime = 28800 [email protected]:~# upsdrvctl start Network UPS Tools - UPS driver controller 2.7.4.1 Network UPS Tools - Generic Q* USB/Serial driver 0.39 (2.7.4.1) USB communication driver 0.43 Subdriver 'hunnox' not found! Driver failed to start (exit status=1) If i remove the subdriver line from ups.conf i can get this [email protected]:~# upsc [email protected] battery.charge: 1 battery.packs: 6 battery.runtime: 37 battery.voltage: 0.00 battery.voltage.high: 13 battery.voltage.low: 11 battery.voltage.nominal: 12.7 device.type: ups driver.name: nutdrv_qx driver.parameter.chargetime: 28800 driver.parameter.offdelay: 60 driver.parameter.ondelay: 180 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.productid: 0000 driver.parameter.runtimecal: 480,100,1200,50 driver.parameter.synchronous: no driver.parameter.vendorid: 0001 driver.version: 2.7.4.1 driver.version.data: Q1 0.07 driver.version.internal: 0.39 driver.version.usb: libusb-1.0.24 (API: 0x1000107) input.frequency: 0.0 input.voltage: 0.0 input.voltage.fault: 0.0 output.voltage: 0.0 ups.beeper.status: disabled ups.delay.shutdown: 60 ups.delay.start: 180 ups.load: 0 ups.productid: 0000 ups.status: OL ups.temperature: 0.0 ups.type: online ups.vendorid: 0001 I tried compiling from git in ubuntu but its a bit out of my league for the moment. Cheers Ok ive figured out the compiling in an Ubuntu VM and moved drivers over to a new txz like @IGHOR did, i think. but i get an error when trying upsdrvctl start [email protected]:~# upsdrvctl start Network UPS Tools - UPS driver controller 2.7.4.1 /usr/libexec/nut/nutdrv_qx: /lib64/libc.so.6: version `GLIBC_2.34' not found (required by /usr/libexec/nut/nutdrv_qx) Driver failed to start (exit status=1) any ideas ? Quote Link to comment
k1netic Posted August 21, 2022 Share Posted August 21, 2022 18 hours ago, k1netic said: Ok ive figured out the compiling in an Ubuntu VM and moved drivers over to a new txz like @IGHOR did, i think. but i get an error when trying upsdrvctl start [email protected]:~# upsdrvctl start Network UPS Tools - UPS driver controller 2.7.4.1 /usr/libexec/nut/nutdrv_qx: /lib64/libc.so.6: version `GLIBC_2.34' not found (required by /usr/libexec/nut/nutdrv_qx) Driver failed to start (exit status=1) any ideas ? If anyone gets to this point, GLIBC_2.34 is available in unraid 6.11.0.rc3 at time of posting This allows you to use nut 2.8.0, but strangely i can now download the file posted by @IGHOR and this was a better option than running an rc3 build. I now have my UPS digitech 650va communicating with NUT using the following [ups] driver = nutdrv_qx port = auto subdriver = hunnox productid = 0000 vendorid = 0001 product = "MEC0003" protocol = hunnox langid_fix = 0x409 novendor noscanlangid default.battery.voltage.high = 13.7 default.battery.voltage.low = 11 default.battery.voltage.nominal = 12.7 runtimecal = 480,100,1200,50 chargetime = 28800 ondelay = 180 offdelay = 60 Cheers Quote Link to comment