I changed batteries very recently in my APC Back-UPS RS 800.  Charging was fine - the batteries were dead, confirmed by trying them in another UPS.   To do the recalibration is quite simple. [*]To avoid surprises (just in case) take the server off-line by stopping the array. [*]In the UPS settings you then stop the APCUPSD daemon, and apply. [*]Assuming that you have a keyboard and monitor attached to your server, at the command line you then run "apctest". (or you can run from a re