dogmanky Posted June 3, 2010 Share Posted June 3, 2010 I used unmenu pkg mgr to install the APC package, but I need to figure out how much load my Tower is using on the UPS. I'd like to plug a couple other things in the UPS. Link to comment
Joe L. Posted June 3, 2010 Share Posted June 3, 2010 I used unmenu pkg mgr to install the APC package, but I need to figure out how much load my Tower is using on the UPS. I'd like to plug a couple other things in the UPS. Many of the UPS have status reports will give you the load. When I run the /sbin/apcaccess status command, either at a linux prompt when logged in, or by pressing the "UPS Status" button on the System-Info tab in unMENU, I can see the load-percentage. I can also see the nominal wattage of my UPS. Below is my output. My UPS on the unRAID server is a 450 Watt nominal unit. It is reporting it is at 55% of capacity with all 15 of my disks spinning. To figure out the actual current drawn is just a bit of basic math. (450 * .55 = 247.5 watts ) Just be aware that the disks can draw a lot more when spinning up to speed at the same time, and they will all need to spin up in order to be unmounted to shut down the server cleanly, so you would want to take a conservative approach on loading the UPS. UPS Status (from /sbin/apcaccess status) APC : 001,038,0940 DATE : Thu Jun 03 11:58:36 EDT 2010 HOSTNAME : Tower RELEASE : 3.14.3 VERSION : 3.14.3 (20 January 2008) slackware UPSNAME : Tower CABLE : Custom Cable Smart MODEL : Back-UPS ES 750 UPSMODE : Stand Alone STARTTIME: Mon May 31 15:13:25 EDT 2010 STATUS : ONLINE LINEV : 120.0 Volts LOADPCT : 55.0 Percent Load Capacity BCHARGE : 100.0 Percent TIMELEFT : 10.9 Minutes MBATTCHG : 10 Percent MINTIMEL : 5 Minutes MAXTIME : 300 Seconds SENSE : Medium LOTRANS : 092.0 Volts HITRANS : 139.0 Volts ALARMDEL : Always BATTV : 13.8 Volts LASTXFER : Low line voltage NUMXFERS : 0 TONBATT : 0 seconds CUMONBATT: 0 seconds XOFFBATT : N/A SELFTEST : NO STATFLAG : 0x07000008 Status Flag MANDATE : 2008-01-13 SERIALNO : 3B0802X63649 BATTDATE : 2001-09-25 NOMINV : 120 Volts NOMBATTV : 12.0 Volts NOMPOWER : 450 Watts FIRMWARE : 841.I2 .D USB FW:I2 APCMODEL : Back-UPS ES 750 END APC : Thu Jun 03 11:58:36 EDT 2010 Link to comment
dogmanky Posted June 3, 2010 Author Share Posted June 3, 2010 Thanks Joe. I should have looked in the unmenu options first. Link to comment
Joe L. Posted June 3, 2010 Share Posted June 3, 2010 Thanks Joe. I should have looked in the unmenu options first. It has a lot of stuff built into it, that's for sure. Lots of people have made suggestions and contributions of their code and configuration files for additional packages, and it really evolved into a pretty useful addition. What UPS do you have? What does it show as its "status" report? Joe L. Link to comment
dogmanky Posted June 3, 2010 Author Share Posted June 3, 2010 Thanks Joe. I should have looked in the unmenu options first. It has a lot of stuff built into it, that's for sure. Lots of people have made suggestions and contributions of their code and configuration files for additional packages, and it really evolved into a pretty useful addition. What UPS do you have? What does it show as its "status" report? Joe L. ES-750 Everything here look normal? (drives all sleeping) APC : 001,038,0946 DATE : Thu Jun 03 13:16:18 GMT+5 2010 HOSTNAME : Tower RELEASE : 3.14.3 VERSION : 3.14.3 (20 January 2008) slackware UPSNAME : Tower CABLE : Custom Cable Smart MODEL : Back-UPS ES 750 UPSMODE : Stand Alone STARTTIME: Tue Jun 01 17:38:48 GMT+5 2010 STATUS : ONLINE LINEV : 118.0 Volts LOADPCT : 16.0 Percent Load Capacity BCHARGE : 100.0 Percent TIMELEFT : 27.6 Minutes MBATTCHG : 10 Percent MINTIMEL : 5 Minutes MAXTIME : 300 Seconds SENSE : Medium LOTRANS : 092.0 Volts HITRANS : 139.0 Volts ALARMDEL : Always BATTV : 13.7 Volts LASTXFER : Low line voltage NUMXFERS : 0 TONBATT : 0 seconds CUMONBATT: 0 seconds XOFFBATT : N/A SELFTEST : NO STATFLAG : 0x07000008 Status Flag MANDATE : 2009-12-27 SERIALNO : 3B0952X42851 BATTDATE : 2001-09-25 NOMINV : 120 Volts NOMBATTV : 12.0 Volts NOMPOWER : 450 Watts FIRMWARE : 841.I3 .D USB FW:I3 APCMODEL : Back-UPS ES 750 END APC : Thu Jun 03 13:16:50 GMT+5 2010 Link to comment
Joe L. Posted June 3, 2010 Share Posted June 3, 2010 It is the same unit I have, only a year newer, and more lightly loaded. Mine has worked wonderfully for the past few years... Looks like you found the UPS Status button. Which of the two APCUPSD packages did you install? The older release?, or the newer? I tried the newer, and ended up at one point after a few weeks where I could not get a status report from the UPS. I'm back to using the older version now, and will try again at some point with the newer once I move some disks off of the server. I did not want to take chances with the UPS losing communications with the server. Joe L. Link to comment
dogmanky Posted June 3, 2010 Author Share Posted June 3, 2010 Which of the two APCUPSD packages did you install? The older release?, or the newer? Joe L. I just installed the older one. Considering the purpose, I decided to just go with something tried and tested. I'll run another status the next time all 19 drives spin up. Link to comment
Joe L. Posted June 3, 2010 Share Posted June 3, 2010 Which of the two APCUPSD packages did you install? The older release?, or the newer? Joe L. I just installed the older one. Considering the purpose, I decided to just go with something tried and tested. I'll run another status the next time all 19 drives spin up. I feel the same way... And just to make you feel good, this is in my syslog as of a bit under two hours ago: Jun 3 12:24:07 Tower apcupsd[1837]: Power failure. Jun 3 12:24:08 Tower apcupsd[1837]: Power is back. UPS running on mains. Apparently a tiny power glitch... I did not notice it, but the UPS did. Joe L. Link to comment
dogmanky Posted June 3, 2010 Author Share Posted June 3, 2010 Joe, I'm at 38% load with all 19 disks spinning.. i have 16 of them in the same spin up group, 2 in another and the parity. Do you think I have any room to plug up anything else to the UPS? Link to comment
Joe L. Posted June 4, 2010 Share Posted June 4, 2010 Joe, I'm at 38% load with all 19 disks spinning.. i have 16 of them in the same spin up group, 2 in another and the parity. Do you think I have any room to plug up anything else to the UPS? I guess it depends on what else it is. Don't forget, they will ALL spin up at the same time when you go to stop the array. Joe L. Link to comment
chrissi5120 Posted May 7, 2013 Share Posted May 7, 2013 sorry for bringing up this old thread but i would like to read my power draw this is what i got: APC : 001,042,1063 DATE : Tue May 07 20:26:48 CEST 2013 HOSTNAME : storageserver RELEASE : 3.14.3 VERSION : 3.14.3 (20 January 2008) slackware UPSNAME : storageserver CABLE : Custom Cable Smart MODEL : Smart-UPS 750 RM UPSMODE : Stand Alone STARTTIME: Tue May 07 19:55:36 CEST 2013 STATUS : ONLINE LINEV : 237.6 Volts LOADPCT : 33.8 Percent Load Capacity BCHARGE : 100.0 Percent TIMELEFT : 34.0 Minutes MBATTCHG : 50 Percent MINTIMEL : 5 Minutes MAXTIME : 300 Seconds OUTPUTV : 237.6 Volts SENSE : High DWAKE : -01 Seconds DSHUTD : 090 Seconds LOTRANS : 208.0 Volts HITRANS : 253.0 Volts RETPCT : 000.0 Percent ITEMP : 17.5 C Internal ALARMDEL : Always BATTV : 27.7 Volts LINEFREQ : 50.0 Hz LASTXFER : No transfers since turnon NUMXFERS : 0 TONBATT : 0 seconds CUMONBATT: 0 seconds XOFFBATT : N/A SELFTEST : NO STATFLAG : 0x07000008 Status Flag SERIALNO : AS1010140588 BATTDATE : 2010-03-02 NOMOUTV : 230 Volts NOMBATTV : 24.0 Volts FIRMWARE : 668.19.I USB FW:11. APCMODEL : Smart-UPS 750 RM END APC : Tue May 07 20:26:58 CEST 2013 the "nompower" field is missing ? what can i do to get the correct value ? best regards Christoph Link to comment
garycase Posted May 7, 2013 Share Posted May 7, 2013 The APC UPS package can only show what's being communicated from the UPS. I'm surprised the SmartUPS doesn't show the "Nompower" field -- but I don't think you can do anything about it. Perhaps the 220v units have slightly different status info. Mine looks fine: (from /sbin/apcaccess status)APC : 001,039,1013 DATE : Tue May 07 13:37:11 CDT 2013 HOSTNAME : JMCBakup RELEASE : 3.14.3 VERSION : 3.14.3 (20 January 2008) slackware UPSNAME : JMCBakup CABLE : Custom Cable Smart MODEL : Back-UPS RS 700G UPSMODE : Stand Alone STARTTIME: Wed Apr 24 04:39:11 CDT 2013 STATUS : ONLINE LINEV : 121.0 Volts LOADPCT : 6.0 Percent Load Capacity BCHARGE : 100.0 Percent TIMELEFT : 70.7 Minutes MBATTCHG : 10 Percent MINTIMEL : 5 Minutes MAXTIME : 300 Seconds SENSE : Medium LOTRANS : 088.0 Volts HITRANS : 141.0 Volts ALARMDEL : Always BATTV : 13.7 Volts LASTXFER : Low line voltage NUMXFERS : 2 XONBATT : Tue Apr 30 05:20:48 CDT 2013 TONBATT : 0 seconds CUMONBATT: 4 seconds XOFFBATT : Tue Apr 30 05:20:50 CDT 2013 SELFTEST : NO STATFLAG : 0x07000008 Status Flag MANDATE : 2012-06-30 SERIALNO : 3B1226X38978 BATTDATE : 2001-09-25 NOMINV : 120 Volts NOMBATTV : 12.0 Volts NOMPOWER : 420 Watts FIRMWARE : 856.L3 .D USB FW:L3 APCMODEL : Back-UPS RS 700G END APC : Tue May 07 13:37:41 CDT 2013 Link to comment
garycase Posted May 7, 2013 Share Posted May 7, 2013 the "nompower" field is missing ? Note: There is a firmware update for your UPS model, dated 12/03/2012, on the APC site. I tend to be an "if it ain't broke, don't fix it" kind of guy -- but if you want to register with APC and download the update, it may very well add the additional information fields to the status info Link to comment
chrissi5120 Posted May 7, 2013 Share Posted May 7, 2013 whoa updates for that kind of usv ? UNBELIEVABLE ! I totally understand your way of never touching a running system, but i am also very corious I will give that a try later thank you very very much best regards Christoph Link to comment
garycase Posted May 7, 2013 Share Posted May 7, 2013 Post a note and let us know if the firmware update adds any additional status -- just curious Link to comment
jeff.lebowski Posted May 9, 2013 Share Posted May 9, 2013 Which of the two APCUPSD packages did you install? The older release?, or the newer? Joe L. I just installed the older one. Considering the purpose, I decided to just go with something tried and tested. I'll run another status the next time all 19 drives spin up. I feel the same way... And just to make you feel good, this is in my syslog as of a bit under two hours ago: Jun 3 12:24:07 Tower apcupsd[1837]: Power failure. Jun 3 12:24:08 Tower apcupsd[1837]: Power is back. UPS running on mains. Apparently a tiny power glitch... I did not notice it, but the UPS did. Joe L. I had a glitch a few days ago. All three servers are plugged into the same 20amp circuit on separate UPS units, but only Subdivisions had its power interrupted. Link to comment
chrissi5120 Posted May 9, 2013 Share Posted May 9, 2013 Post a note and let us know if the firmware update adds any additional status -- just curious mmmh APC.. that hurts... is there any way to update that damn beast in unraid ? I think I won't get to the point where I install windows on my laptop (or even VM), walk down the stairs and update the firmware this way ?! best regards Christoph Link to comment
Joe L. Posted May 9, 2013 Share Posted May 9, 2013 Post a note and let us know if the firmware update adds any additional status -- just curious mmmh APC.. that hurts... is there any way to update that damn beast in unraid ? I think I won't get to the point where I install windows on my laptop (or even VM), walk down the stairs and update the firmware this way ?! best regards Christoph I would never update the firmware on the UPS unless you knew what it affected. You might give APC a call a find out. There is no way to give a parameter the UPS cannot supply. As I said, a wattmeter is FAR easier to attach and figure out the load. (besides, you already have a good idea based on the LOADPCT. Link to comment
garycase Posted May 9, 2013 Share Posted May 9, 2013 Post a note and let us know if the firmware update adds any additional status -- just curious mmmh APC.. that hurts... is there any way to update that damn beast in unraid ? I think I won't get to the point where I install windows on my laptop (or even VM), walk down the stairs and update the firmware this way ?! best regards Christoph I would never update the firmware on the UPS unless you knew what it affected. You might give APC a call a find out. There is no way to give a parameter the UPS cannot supply. As I said, a wattmeter is FAR easier to attach and figure out the load. (besides, you already have a good idea based on the LOADPCT. I absolutely agree with Joe L ==> your UPS is working fine; any firmware update will, at most, simply add another bit of status info that you don't really need ... and as with any firmware based device, a bad flash could effectively destroy the unit !! As I noted earlier, "... I tend to be an "if it ain't broke, don't fix it" kind of guy " Link to comment
chrissi5120 Posted May 10, 2013 Share Posted May 10, 2013 you're right guys My UPS is markes as 750VA 480W, so can i do that simple math ? LOADPCT x 480W = Load in Watt 0.27 x 480W = 129,6 W ? best regards Christoph Link to comment
garycase Posted May 10, 2013 Share Posted May 10, 2013 LOADPCT x 480W = Load in Watt 0.27 x 480W = 129,6 W ? Yes, that's correct. An even better way to know what your system is using -- which will include any UPS "overhead" (the UPS itself draws a small amount of power) -- is to use a Kill-a-Watt, a VERY handy little gadget that everyone should have http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001 Link to comment