October 23, 20232 yr Hi everyone, I bought this new UPS from Amazon 3 days ago: APC Back-UPS BX1200MI. I turned it on and unraid immediately recognized it, the problem is that occasionally, I get the notification of battery problems, but I don't see any errors. I tried to run the UPS self test and it didn't give any errors. I tried connecting it to a Windows PC and running the test from its proprietary software and it didn't give any errors. I tried turning off the power and it worked fine for the first 4 minutes, then in unraid it alarmed again and made unraid shut down. I then tried to turn off the power and connecting the USB to the Windows PC to monitor with the proprietary software and it didn't give any type of error for more than 20 minutes. When it reached around 50% battery I turned the power back on. Anyone have any ideas? Could it be due to the date of the batteries which is reported as 2001-01-01? If the product is new and never used, is this a problem? Can I simulate a battery replacement today by telling the UPS that I changed them to see if the error was caused only by the old date? Can it be done from unraid or do I have to use its software? I add that the battery always remains at 99% after 3 days and does not reach 100% so I cannot do the calibration from apctest. Thanks
October 23, 20232 yr 1 hour ago, ilpixelmatto said: Could it be due to the date of the batteries which is reported as 2001-01-01? Not relate. You should got a mfg test report in package, check the mfg date. Your problem likely because "low line voltage" and have 417 times transfer to battery. This also may be the reason why battery does not reach 100%. Edited October 23, 20232 yr by Vr2Io
October 23, 20232 yr Author 6 minutes ago, Vr2Io said: Not relate. You should got a mfg test report in package, check the mfg date. Your problem likely because "low line voltage" and have 417 times transfer to battery. This also be the reason why battery does not reach 100%. I didn't understand the thing about the mfg test report in package, where can I find it? Now the low line voltage is at 23
October 23, 20232 yr A paper slip inside the package. 11 minutes ago, ilpixelmatto said: Now the low line voltage is at 23 23 ? LOTRANS was 145v, so if line voltage below that, it will switch to battery. Edited October 23, 20232 yr by Vr2Io
October 23, 20232 yr Author 18 minutes ago, Vr2Io said: A paper slip inside the package. 23 ? LOTRANS was 145v, so if line voltage below that, it will switch to battery. I don't have any sheet with tests performed on the UPS, perhaps they aren't performed in Italy, or they aren't included on Amazon. The 23 referred to the value of NUMXFERS. I tried setting the sensitivity to low, to see if it switches to battery less often. My only doubt is to understand if it is a faulty UPS or not, APC's powerchute software does not detect any problem, it runs the selftest and passes, by turning off the power on unraid it says "running on batteries" and it only happens for an instant "Batteries have failed on UPS" then goes back to running on batteries without giving any more errors. However, this is enough to trigger the shutdown. If I turn off the monitoring from unraid, the UPS holds up without visible errors (from the LEDs) for over 20-30 minutes.
October 23, 20232 yr Solution 25 minutes ago, ilpixelmatto said: UPS holds up without visible errors (from the LEDs) for over 20-30 minutes. Base on that, it doesn't like UPS nor battery have problem, suggest turn off APCUPSD and install NUT for troubleshoot why APCUPSD will interpret the battery were fault and shutdown immediate. ( NUT can setting don't shutdown, so you can further troubleshoot ** pls stop array for safe ** ) After you disable all UPS monitoring, you can in command prompt type APCTEST to set battery date or perform selftest. And you need fix why NUMXFERS so often !!! ( Of cause, it may UPS fault ) Edited October 23, 20232 yr by Vr2Io
October 25, 20232 yr Author Hi, a little update, I switched to NUT as suggested, the problem was partially solved, now doing some tests, I stopped the array, turned off the power and the UPS kept the system on for over 30 minutes, once reached 25% battery, it turned off as scheduled. Sometrimes the "battery have failed" error is triggered but it disappears immediately afterwards. All self tests continue to pass without problems. However, I discovered why NUMXFERS is so high, the voltage in my house should be 220 volts, but often it is 240-245 volts, this unfortunately causes the UPS to regulate the voltage which I think is the reason why it doesn't reach never 100%. I'll try keeping the UPS on charge with nothing connected, to see if it gets to 100%.
January 18, 20242 yr @ilpixelmatto any updates on this? I have bought the APC Back-UPS BX750MI and am experiencing the same battery failed error in Unraid. Will post details screenshot shortly.
January 18, 20242 yr Author 3 hours ago, tommyb10 said: @ilpixelmatto any updates on this? I have bought the APC Back-UPS BX750MI and am experiencing the same battery failed error in Unraid. Will post details screenshot shortly. Hi, after all these months since I created the post, I continue to have the problem, although more occasionally. It happens to me once every 2-5 days. However, with management via NUT I solved the problem relating to premature shutdown. NUT gives a notification, but does not shut down the server. Mine is a somewhat particular case perhaps and these notifications are probably also caused by my home current which is 245V and not 230V, but so far I have never had any problems or sudden shutdowns. You can try doing the test and see how long it lasts on, but please stop the array before doing so.
January 19, 20242 yr 16 hours ago, ilpixelmatto said: Hi, after all these months since I created the post, I continue to have the problem, although more occasionally. It happens to me once every 2-5 days. However, with management via NUT I solved the problem relating to premature shutdown. NUT gives a notification, but does not shut down the server. Mine is a somewhat particular case perhaps and these notifications are probably also caused by my home current which is 245V and not 230V, but so far I have never had any problems or sudden shutdowns. You can try doing the test and see how long it lasts on, but please stop the array before doing so. Strange, I am getting essentially the same battery error, but 2-3 times per day at the moment. 0 NUMXFERS and 100% battery. This screenshot is from a few minutes after one of the notifications.
February 2, 20242 yr i just bought a new BX1200MI, and has the same issues. As I have tested, battery fail reports only if usb attached to Unraid, attached to a Win laptop, through Powerchute, I cannot reproduce the error, neither self test fail. I have tried too the apctest, but self test fails, calibration fails, but through Powerchute, succeeds, without issue. Seems like a communication issue with this serie of ups with Unraid??? (have the same outcome with NUT too) I am running out of ideas, because ups works fine, not sure if it should be returned or just ignore the errors it gives to Unraid. **Update** I have connected the UPS to Powerchute and disabled the warning for battery, then connected back, I am still getting the errors Edited February 13, 20242 yr by zsoltsuhajda
March 29, 20242 yr I also have problems with BX750MI reporting battery fault condition, maybe some incompatibility with the BX line up. Brought 2 new units in spring sale, 1 is connected to QNAP464, Other to new Unraid Server QNAP seems happy with it and reports no issues 100% battery, Unraid flagging its one multiple times a day and shows 99% battery. When I finally finish transferring all my data I might swap them over see where the fault follows.
April 4, 20242 yr On 2/2/2024 at 4:56 PM, zsoltsuhajda said: i just bought a new BX1200MI, and has the same issues. As I have tested, battery fail reports only if usb attached to Unraid, attached to a Win laptop, through Powerchute, I cannot reproduce the error, neither self test fail. I have tried too the apctest, but self test fails, calibration fails, but through Powerchute, succeeds, without issue. Seems like a communication issue with this serie of ups with Unraid??? (have the same outcome with NUT too) I am running out of ideas, because ups works fine, not sure if it should be returned or just ignore the errors it gives to Unraid. **Update** I have connected the UPS to Powerchute and disabled the warning for battery, then connected back, I am still getting the errors any updates? getting the same errors lol
April 4, 20242 yr Author Update: I actually never solved the problem. I used NUT to manage the UPS, every 1-3 days I am notified of the error but I don't notice any problems. If the power goes out, the server follows the directions I set without errors.
April 4, 20242 yr The APC BX series seems to have a firmware (or compatibility) issue affecting both APCUPSD ("UPS Settings") and NUT. Symptoms of this issue include common low battery notifications, despite the UPS being online/fully charged, as well as frequent battery replacement notifications and increasing NUMXFERS. The situation on APCUPSD seems more severe as unwanted shutdowns have been reported by affected users as well. It is therefore recommended to use NUT for this affected UPS series, where the problem also appears but is seemingly limited to wrongful low battery and battery replacement events being reported in the SYSLOG but the UPS functioning normally otherwise (including on battery notifications and graceful shutdowns from power events). It is possible to disable battery replacement notifications in NUT's settings, so the falsely reported events would be limited to the SYSLOG and a minor annoyance rather than a deal-breaker rendering the UPS entirely unusable on Unraid. If you have been using NUT before: It is recommended to first "Reset Config" in the NUT Settings before setting up NUT again, as an existing configuration might be stored on your USB still. This ensures starting with a fresh configuration where this issue has been taken into consideration, as opposed to older legacy configurations reporting such false low battery events through Unraid's notification services often. The respective issues can be found here: https://sourceforge.net/p/apcupsd/mailman/message/58740970/ (APCUPSD) https://github.com/networkupstools/nut/issues/2347 (NUT) Edited April 4, 20242 yr by Rysz
April 8, 20242 yr Guys, I just had a "Lost connection to UPS" notification on Unraid. Then I put the USB cable from a 3.2 port to a 3.1 port. The connection has been reestablished afterwards. Also, the battery charge went from 99% to 100%, and I am not getting the "Battery have failed..." notification anymore (Got them like 10 times a day). Additionally, the NUMXFERS count stays at 0 now, it went up beyond the 1000s before. Please try switching the USB cable to a different or lower USB port. Maybe that will work for you guys too @ilpixelmatto@tommyb10@Vr2Io@zsoltsuhajda@LSL1337@ogr@RZR911
May 29, 20242 yr Community Expert On 4/9/2024 at 7:25 AM, wulperdinger said: Guys, I just had a "Lost connection to UPS" notification on Unraid. Then I put the USB cable from a 3.2 port to a 3.1 port. The connection has been reestablished afterwards. Also, the battery charge went from 99% to 100%, and I am not getting the "Battery have failed..." notification anymore (Got them like 10 times a day). Additionally, the NUMXFERS count stays at 0 now, it went up beyond the 1000s before. Please try switching the USB cable to a different or lower USB port. Maybe that will work for you guys too @ilpixelmatto@tommyb10@Vr2Io@zsoltsuhajda@LSL1337@ogr@RZR911 Thanks for this - I was upset I had the same problem as this - plugged into an old USB instead of the keyboard and now showing 100% - hopefully the errors go now too.
May 30, 20242 yr Community Expert Further to this, mine is also 100% after swapping the cable to old USB port, but I am still seeing this in the logs over and over - filling them up : May 30 12:04:50 Tower apcupsd[26285]: Battery disconnected. May 30 12:04:51 Tower apcupsd[26285]: Battery reattached. May 30 12:07:15 Tower apcupsd[26285]: Battery disconnected. May 30 12:07:16 Tower apcupsd[26285]: Battery reattached. May 30 12:09:28 Tower apcupsd[26285]: Battery disconnected. May 30 12:09:29 Tower apcupsd[26285]: Battery reattached. May 30 12:10:42 Tower apcupsd[26285]: Battery disconnected. May 30 12:10:42 Tower apcupsd[26285]: Battery reattached. May 30 12:10:47 Tower apcupsd[26285]: Battery disconnected. May 30 12:10:48 Tower apcupsd[26285]: Battery reattached. May 30 12:11:27 Tower apcupsd[26285]: Battery disconnected. May 30 12:11:28 Tower apcupsd[26285]: Battery reattached. May 30 12:11:29 Tower apcupsd[26285]: Battery disconnected. May 30 12:11:30 Tower apcupsd[26285]: Battery reattached. May 30 12:13:40 Tower apcupsd[26285]: Battery disconnected. May 30 12:13:41 Tower apcupsd[26285]: Battery reattached. May 30 12:15:33 Tower apcupsd[26285]: Battery disconnected. May 30 12:15:34 Tower apcupsd[26285]: Battery reattached. May 30 12:17:11 Tower apcupsd[26285]: Battery disconnected. May 30 12:17:12 Tower apcupsd[26285]: Battery reattached. May 30 12:17:29 Tower apcupsd[26285]: Battery disconnected. May 30 12:17:30 Tower apcupsd[26285]: Battery reattached. May 30 12:17:41 Tower apcupsd[26285]: Battery disconnected. May 30 12:17:42 Tower apcupsd[26285]: Battery reattached.
May 30, 20242 yr 1 hour ago, vw-kombi said: Further to this, mine is also 100% after swapping the cable to old USB port, but I am still seeing this in the logs over and over - filling them up : May 30 12:04:50 Tower apcupsd[26285]: Battery disconnected. May 30 12:04:51 Tower apcupsd[26285]: Battery reattached. May 30 12:07:15 Tower apcupsd[26285]: Battery disconnected. May 30 12:07:16 Tower apcupsd[26285]: Battery reattached. May 30 12:09:28 Tower apcupsd[26285]: Battery disconnected. May 30 12:09:29 Tower apcupsd[26285]: Battery reattached. If you confirm UPS functional normal ( putting on battery mode ) by press UPS physical button, then it should be USB port or APCUPSD / NUT issue. Pls try APCUPSD / NUT both, if still got issue, I will suggest add a USB hub ( best USB 2.0 ) between them. Edited May 30, 20242 yr by Vr2Io
May 30, 20242 yr Community Expert Seems to be an issue with the APCupsd and the new APC firmwares. I have stopped this in unraid, moved to NUT, then put a nut client on my home assistant so i can still report UPS power use. No issue since doing that.
June 9, 20251 yr bummer, only found this thread after buying a BX1200MI for my NAS and immediately getting this error and googling it to end up here.I started with it connected to a USB 2.0 port - I've switched to a 3.2 gen 1 port and will see if that makes any difference. if the error can be safely ignored, then whatever, but i'm not sure if the increasing NUMXFERS are normal or part of this bug as some other posts suggest - it seems to be doing a self test every 5 minutes, which doesn't seem crazy to me?UPDATE: this might help some others - I am pretty sure my motherboard uses an Asmedia controller for the USB 2.0 ports, and the one 3.2 Gen 1 port it has. I had this issue manifest with the UPS on all these ports.I switched to the motherboard's USB 3.2 Gen 2 ports, which, from reviewing lsusb, go directly via the Intel B660 chipset. As soon as I switched to one of these ports, I noticed the same thing as other posters: the UPS went to 100% (from 99%), and NUMXFERS stopped iterating. The automatic self tests I was seeing every 5 minutes have stopped as well, so CUMONBATT has not gone up either.So take a look at what USB controller you're connecting it via. But most importantly it looks like, at least in my case, it's unnecessarily performing self tests while the issue manifests.UPDATE 2: I'm getting, on Unraid via apcupsd, the behaviour people above described when using NUT on separate infra to manage the UPS. So I am still getting the battery failure warnings using the USB port that goes directly via the Intel controller, but NUMXFERS and CUMONBATT have not gone up at all since switching to this port, and charge remains at 100%. Hope this helps someone else. Edited June 11, 20251 yr by auiayuiox
March 17Mar 17 Brand new APC 750 VA / 410 Watt and i'm getting the "Batteries have failed on UPS" error. Should I return it and get other brand?