V6 Plugin for APC UPS


mr_cb7

Recommended Posts

Has anyone seen odd issues with the built in one?

I have not had issues with the v5 APC UPS driver - the v6 one seems to always display around 0.76 minutes to 2.25 minutes left.

 

It is a APC UPS backup-pro 750, 27% load and on v5 42minute runtime. all other stats are as before.

In one case unraid shutdown based on the UPS state.

 

Right now I have the runtime setting set to 0 in hopes it disables that check.

 

Link to comment

Has anyone seen odd issues with the built in one?

I have not had issues with the v5 APC UPS driver - the v6 one seems to always display around 0.76 minutes to 2.25 minutes left.

How old is your battery? Typical life is between 2-4 years, but sometimes less. A cell gone bad in the UPS battery will severely cut down runtime, and the UPS is able to sense that.
Link to comment
  • 4 weeks later...

Think may have this one solved. It appears to be a APC UPS issue. Around the same time as my v5 -> v6 upgrade I swapped a new battery in. In some cases the APC will have a brain fart and get confused. Under windows the APC app would do a calibration, for apcupd a manual calibration is required.

 

I just swapped it with another APC unit I had and it works fine now

 

Link to comment

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.